PAL-S08(4-Channel Temperature Input Module)

Topic: PAL015

Use the information in the table below to configure the parameters for the PAL S08 4-Channel Temperature Input Module.

 

Setting

Options

How It Works

Setting Description

Unit of Measurement

Celsius (default)

Fahrenheit

Select between Celsius and Fahrenheit as the temperature format for the module.

Module setting for temperature format.

Noise Suppression

50Hz (default)

60Hz

50/60Hz slow

50/60Hz fast

This is a module setting to choose between better filtering or faster update.

Suppresses noise generated by main electrical supply. 50/60Hz slow delivers a high level of filtering, but updates the channels more slowly. 50/60Hz fast delivers less filtering, but updates the channels faster.

Sensor Type

No sensor (default)

Pt100 (TK=0.00385)

Pt200 (TK=0.00385)

Pt500 (TK=0.00385)

Pt1000 (TK=0.00385)

Pt100 (TK=0.00391)

Pt200 (TK=0.00391)

Pt500 (TK=0.00391)

Pt1000 (TK=0.00391)

Ni100 (TK=0.00617)

Ni200 (TK=0.00617)

Ni500 (TK=0.00617)

Ni1000 (TK=0.00617)

TC Type E

TC Type J

TC Type T

TC Type K

TC Type N

TC Type S

TC Type B

TC Type R

Choose between the different available RTD and Thermocouple types. Choose 0 to disable the channel. It is recommended to disable unused channels to save on processing time.

Types of sensors and thermocouples the module supports. Set all unused channels to No sensor to save on processing time.

Connection Type

2 wires (default)

3 wires

4 wires

Selects the number of wires that the sensor has. This is primarily a factor for RTDs.

Each channel provides 4 pins:

  • Sensor Power +
  • Sensor Power -
  • Input signal + and
  • Input signal -.

Choose the number of wires that the sensor requires for this channel.

 

Resolution Parameters

CJC Compensation:

External (default)

Internal

There is an internal CJC provided with the module, but in some applications with some sensor types (such as with the Pt1000), an external CJC may work better.

There is an internal Cold Junction Compensation but it may be better to use an external CJC for cases where sudden temperature changes occur such as with the Pt1000.

Resolution:

0.1 (default)

0.01

Determines the resolution of the temperature reading and only applies to RTD sensors with temperature reading range of +/- 327 C.

Choose the resolution of temperature display. This only applies to RTD sensors with temperature reading range of +/- 327 C.

Filter:

Sync 3 (default)

Sync 4

This digital filter setting works in conjunction with the module Noise Suppression filter. Sync4 provides greater filtering than Sync3, but has slower updates.

The digital filter setting that works in conjunction with the Noise Suppression filter. Sync4 provides greater filtering but slower updates than Sync3.

Filter Diagnostic Parameters

Filter setting:

No Filter (default)

1 sample

2 samples

4 samples

8 samples

16 samples

32 samples

64 samples

This option determines the number of samples that are averaged. The greater the value, the steadier the value but the slower the update.

Filter Setting determines the number of samples that are acquired before updating the digital value. The higher the samples, the greater the filtering but slower updates.

Max Value Monitor:

Disabled (default)

Enabled

An alarm option to inform the user when the temperature has exceeded a specified value. Enabling this option requires specifying the Maximum temperature value in the field below. If the temperature exceeds the value specified, it will be indicated in Input Byte 0 (status byte). The error data will be between 0xD4 – 0xD7.

Max Value Monitor enables the Max Temperature monitor and will generate an alarm if the value is exceeded. Use the Max Temperature value setting if enabling this option.

Min Value Monitor:

Disabled (default)

Enabled

An alarm option to inform the user when the temperature has dropped below a specified value. Enabling this option requires specifying the Minimum temperature value in the field below. If the temperature is below the value specified, it will be indicated in Input Byte 0 (status byte). The error data will be between 0xD4 – 0xD7.

Min Value Monitor enables the Min Temperature monitor and will generate an alarm if the value is exceeded. Use the Min Temperature value setting if enabling this option.

Short Circuit detect:

Disabled (default)

Enabled

An alarm option to inform the user that a channel has short circuited. If a short circuit is detected, it will be indicated in Input Byte 0 (status byte). The error data will be between 0xD4 – 0xD7.

This option enables Short circuit detection for the channel. An alarm is generated if a short circuit is detected.

Open circuit detect:

Disabled (default)

Enabled

An alarm option to inform the user that a channel has an open circuit. If an open circuit is detected, it will be indicated in Input Byte 0 (status byte). The error data will be between 0xD4 – 0xD7.

This bit enables Open circuit detection for the channel. An alarm is generated if an open circuit is detected.

Minimum Temperature

Valid range for each channel: -32768 to 32767

Default: 1

This value is used in conjunction with the Min Value Monitor to signal an alarm when the temperature has dropped below the value specified in this field. Valid range is -32768 to 32767.

Minimum Temperature value used for the Minimum Temperature detection function.

Maximum Temperature

Valid range for each channel: -32768 to 32767

Default: 127

This value is used in conjunction with the Max Value Monitor to signal an alarm when the temperature has risen above the value specified in this field. Valid range is -32768 to 32767.

Maximum Temperature value used for the Maximum Temperature detection function.